PLUS+1 Update Center / Re: Update Center don't work V1.0.190
« Last post by Tor on June 01, 2026, 07:18:19 AM »
Hello rtapia,

I can see in your case that you got a response May 26 saying that you are running the tool as an Admin?
You should not run the PLUS+1 Update Center as an admin.

Double check your settings and get back to your support person.


Have a nice day.
12
PLUS+1 Update Center / Re: Update Center don't work V1.0.190
« Last post by rtapia on May 29, 2026, 02:20:38 PM »
Hi Tor admin,

yes i registered the case in plus+1 helpdesk from two weeks ago... but, i am still yet a true answer for this... :'(
while, i ask for install the older version of P+1 because i don't need the last version for the development that i need to do.

thanks for your commnet.
13
PLUS+1 Update Center / Re: Update Center don't work V1.0.190
« Last post by Tor on May 29, 2026, 07:27:47 AM »
Hello rtapia,

There are a few users who have not been able to get Update Center up and running with the above solution.
If you have not registered a case with PLUS+1 Helpdesk, please do so.
https://www.danfoss.com/en/campaigns/dps/plusplus1-support-form/

I'm sorry about the inconvenience.
14
PLUS+1 Update Center / Re: Update Center don't work V1.0.190
« Last post by rtapia on May 28, 2026, 06:37:33 PM »
some one more have the same problem ?
15
License / Re: The whole lisencing structure of Danfoss is plain out stupid.
« Last post by samuelhj on May 21, 2026, 10:58:47 PM »
Turns out all those options failed. And I'll be moving on to a different platform from now on.
16
Controllers / Re: Dynamic Node ID - Is this possible?
« Last post by samuelhj on May 21, 2026, 10:34:42 PM »
Hello,

I would like to ask whether it is possible, from PLUS+1 GUIDE code or from an already compiled application, to reset or restart a CAN interface without performing a full power cycle.

The reason is that I need to change the Node ID of a specific CAN interface during operation. The application involves connecting two machines which normally operate independently, but in this case they need to be linked together and behave as one machine in a Master-Slave configuration.

Ideally, I would like to change the Node ID and then restart or reinitialize only the CAN interface, so the new configuration becomes active without switching the whole controller off and on again.

Is this possible in PLUS+1 GUIDE, or is a full power cycle required for the CAN interface to apply the new Node ID?

Thank you for any advice or experience.

This is a terrible idea. For multiple reasons I'm not going to even discuss here. The better solution would to keep the two things seperated by a controller that acts as a gateway between whatever 3rd party is listening and the two nodes. The design of the gateway would be heavily influenced  by what type of application you're applying this to and how the 3way communication should look like.
17
PLUS+1 Compliant Hardware / Re: JS1H - Digi out
« Last post by samuelhj on May 21, 2026, 10:17:29 PM »
With a programmable joystick yes, this is possible, with most of the JS1H variants, you'd need a controller between.
18
PLUS+1 Compliant Hardware / Re: JS1H questions
« Last post by samuelhj on May 21, 2026, 09:07:36 PM »
If you're still working on this and having issues, using the function library (IIRC have to buy it from Danfoss) makes working with PVE and PWM valves much easier.
19
PLUS+1 GUIDE / Re: CAN messages delayed by 10 ms
« Last post by Marbek_Elektronik on May 20, 2026, 08:56:11 AM »
yes, you are right.
The periodic time is maximum +1 loop-time!

Take 10x1ms and not 1x10ms and
take 10x10ms and not 1x100ms.

What ist your loop time?
20
PLUS+1 GUIDE / Re: CAN messages delayed by 10 ms
« Last post by Lukey on May 20, 2026, 08:03:57 AM »
I've had a similar thing happen before, it's related to your .ExecTimeOut:
Found in Pages TOP > Inputs > OS
Default is 10ms which explains the 10ms difference you are seeing.
Try changing it to 1ms and see what happens.