				I have a question. How many Plus 1 controller can be connected to the same bus and work properly? 255 ?
 
 Lijun
- 
				Hi,
 I want to try to give an answer:
 
 It depends on the configuration of your system.
 Somewhere I have read about 15 IO-Modules?
 
 I have build a system with 2 Can-Joysticks, 1 MC050-10, 1 DP250, 1 IX012 3 OX 024
 and the bus traffic was about 60%.
 
 You have to watch the bus traffic.
 
 Controller and Input and Output modules and other modules send every e.g. 20ms information.
 You can change this time to a higher parameter if it is OK for your application.
 So, look to the traffic!
 
 I hope, this helps a little,
 
 Bernd
 
 
- 
				Hi,
 mebib posted a link relevant to this, some time ago.
 
 http://powersolutions.danfoss.com/stellent/groups/publications/documents/product_literature/520l0719.pdf
 on page 21, you will find a nice list of estimated CAN-bus loads for the different controllers.
 
 Regards
 Jakob
 
- 
				Thanks for your reply! I can control the bus load. The concern is hardware that I read from an article which states there is a limit of 110 node on the same bus because of voltage .
 
 best regards
 Lijun
- 
				Interesting, do you have a link to this article?
 I doubt that I would ever need above 110 nodes, but never say never. Even silent nodes are nodes too.
 
 But then maybe another bus would be more suitable.