PLUS+1 Tools => PLUS+1 Service Tool => Topic started by: Thierry_ACE_germany on December 19, 2025, 11:02:42 AM
-
I am using a Kvaser Leaf Light V2, PLus+1 recognises my gateway and shows connected but "Start Communication" is greyed out and no information is populated in the service application.
Do I need a tool key or a genuine CG150-2?
We have used the generic Kvaser gateway in the past without issues.
-
Hello Thierry
I have seen this error message on two occasions (with CG150):
1. If you have two or more ECUs with the same Node ID. >Make sure that all ECUs on the bus has different Node IDs.
2. If you open/connect two PLUS+1 Service Tools on the PC. >Make sure to only have one instance of Service Tool connected to the bus at one time.
I hope this information helped. If not, please contact PLUS+1 Helpdesk. I guess they would like some more information to be able to help. https://www.danfoss.com/en/campaigns/dps/plusplus1-support-form/ (https://www.danfoss.com/en/campaigns/dps/plusplus1-support-form/)
Have a nice Holiday.