 I use Joystick JS6000 was showing in topis https://www.plus1forum.danfoss.com/index.php?topic=1667.msg5580#msg5580.
 
 Joystick is connect to sensor_3Pt.  The Program is working good but I have problem with sensor_3Pt calculation as shown in photo. There are some mistake in manual.
 
 So I want to understand those formulas in order to configured my sensor_3Pt.
 
 Please could you correct the mistake and give us a calculation example as in manual but with more detail and correct.
 
 Thanks in advance you help
 
 With best regards
- 
				Fault % = 500 means 5% or 0.05
 Hi/Lo DBand % 1000 means 10% or 0.1
 Mid DBand % 1000 means 10% or 0.1
 Hi Cal % 9000 means 90% or 0.9
 Mid Cal % 5000 means 50% or 0.5
 Lo Cal % 1000 means 10% or 0.1
 Formulas are correct:
 High DBand starts = SNSRPWR x (HiCal% - HiDBand*(HiCal%-LoCal%)) =
 5000 x (0.9 - 0.1 * ( 0.9 - 0.1)) = 5000 x (0.9 - 0.1 ( 0.8 )) = 5000 ( 0.9 - 0.08 ) = 5000 ( 0.82 ) = 4100
 Middle DBand starts SNSRPWR x (MidCal% - MidDBand*(MidCal%-LoCal%)) =
 5000 x (0.5 - 0.1 * ( 0.5 - 0.1)) = 5000 x (0.5 - 0.1 ( 0.4 )) = 5000 ( 0.5 - 0.04 ) = 5000 ( 0.46 ) = 2300
 Middle DBand Ends SNSRPWR x (MidCal% + MidDBand*(HiCal%-MidCal%)) =
 5000 x (0.5 + 0.1 * ( 0.9 - 0.5)) = 5000 x (0.5 + 0.1 ( 0.4 )) = 5000 ( 0.5 + 0.04 ) = 5000 ( 0.54 ) = 2700
 Low DBand starts = SNSRPWR x (LoCal% - LoDBand*(HiCal%-LoCal%)) =
 5000 x (0.1 + 0.1 * ( 0.9 - 0.1)) = 5000 x (0.1 + 0.1 ( 0.8 )) = 5000 ( 0.1 + 0.08 ) = 5000 ( 0.18 ) = 900
- 
				Hello sir
 
 Thank you very much for your answer but I am not satisfied with your calculations because first your formulas is different than in Sensor_3Pt remark.
 This is Danfoss problem.
 
 First the formulas are different in manual and in plus+1 guide.
 The second Mid Dbnd% and Hi/Lo Dbnd% their range is 5000 but their unit is 0.01%.   I think it must be 0.02%.
 It not possible to be same as LoCal% or MidCal% or HiCall and Fault because their range is 10000  and their unit is 0.01%
 
 In my case if I use Plus+1 guide sensor_3Pt with the yellow remark formula with unit=0.02 as shown in my last picture I found good result as my joystick real measure.  You can see the picture below.
 
 As conclusion
 There are some mistake in manual and in plus +1 guide formula.
 The plus+1 guide sensor_3Pt remark formula is correct but the unit is not correct.  It's most be 0.02.
 Or keep the unit 0.01% but change range from 5000 to 10000.  Depending how it's programmed inside.
 
 I hope Danfoss corrects its mistakes in the future
 
 I also hope that this exercise is beneficial for other users.
 
 With best regards
 
 
 
 
- 
				Hello
 
 It's me again.
 
 Sorry in picture was mistake  1000 is 20% 0.2   and 2000 is 40% 0.4 and  3000 is 60% 0.6
 
 Tank you
 
 Best regards
- 
				Hello
 
 Here is calculation detail see picture.
 
 From those calculates I think the range and unit of sensor_3Pt are 10000 and 0.01.
 
 Both real and calculate result are the same.
 
 With bests regards