FStelzer,
I have not used any of the MC018 however from your description, 15W on 12 V system, the nominal current will be 1.25 amps for resistive loads it is recommended to design 3x your nominal current, for inductive it is recommended to design 5x your system.
a LED is not an inductive load but even with that you are still safe.
now if that was a typo and you meant 150W on 12volts system then that is 12.5 Amps so times 3 it will be 37.5 amps. according with the datasheet of the MC018 the overcurrent for the output is 47.6 amps so you still should be ok.
on the other hand I would try to ramp up the turning of the LED by minimizing the duty cycle and keep it increasing over a few seconds.
I have done that with a MC012 and a SS relay so that I "dimmed" the LED of a LIGHT BAR for off road, as far as I remember the LED LIGHT BAR was like 120W or 150W. it did work pretty well.
I hope this helps