Author Topic: PVED-CC S7 ISOBUS when CAN network is down.  (Read 7053 times)

Offline jert

  • PLUS+1 Novice
  • *
  • Posts: 2
  • Karma: +0/-0
PVED-CC S7 ISOBUS when CAN network is down.
« on: October 18, 2023, 09:44:55 PM »
I have had a failure with our Danfoss PVED-CC S7 valves when the CAN network fails. If the valve was commanded on it keeps going even though the CAN network is down.  Is there a parameter that I can set so that if the valve loses the CAN signal it will stop immediately or go to neutral?

Offline G30RG3

  • PLUS+1 Expert
  • ****
  • Posts: 74
  • Karma: +3/-0
Re: PVED-CC S7 ISOBUS when CAN network is down.
« Reply #1 on: October 19, 2023, 06:55:11 PM »
AFAIK the PVE should generate an error after 250ms.
I guess you've set the fault monitoring to passive?
Setting this to active, should bring the PVE to a safe state in case of an error.