Stefan:
Hello.
Due to a limitation in Update Center will not all files in the Ouster compliance block be installed. Danfoss are working on a solution for this.
It will be installed correct if it is installed manually in GUIDE. Please follow these steps:
1. Uninstall the Ouster compliance block in GUIDE if you have already installed it. Setup>Uninstall>Hardware
2. Under Tools>Options>General in Update Center: Make sure that you have unchecked "Automatically delete installed files". With this setting you can use the installation file from the download folder in Update Center.
3. Under Tool>Options>Storage you will find the Update Center download folder. Default: C:\Danfoss\PLUS1\Update Center\Downloads\
Look for the Ouster install file. If you don't find it please install it again from Update Center.
4. Install the Ouster compliance block manually in GUIDE here: Setup>Install>Hardware.
Now the block should be installed correct
Best regards
Stefan