Post by: G30RG3 on January 20, 2020, 03:53:54 PM
Hi all,

Is there a document telling us how to implement and use the calibration functionality in compliant hardware?
For instance I want to use the calibration function of the H1 pump EDC 24V control.
What do I need to provide in the software to get the possibility to set the threshold and endcurrent of the control.
If done manually, I guess I would send a increasing current to the control and:
 memorize the value at witch the pump starts to deliver as the threshold value,
and the end stroke would be where the servo pressure jumps up to charge pressure...

Is there documentation available on how and what is possible?
Title: Re: Calibration functionality EDC controls
Post by: spittet on January 20, 2020, 06:44:09 PM
Hi,

I think this document will help you : https://assets.danfoss.com/documents/DOC152886481463/DOC152886481463.pdf

It is normally find in PLUS1 GUIDE at this place :

Hardware tab --> Pumps - Hydraulic --> H1 --> H1 EDC --> Sub templates --> H1_24V_CTRL_ --> User Manual


Sam