PLUS+1 Hardware > Controllers
Output Configured for both/either Sinking or Sourcing
(1/1)
Lukey:
Is it possible for an output to function as both Sinking and Sourcing?
I successfully test complied an application that changes the Output mode from 1 to 2 during runtime of the controller.
I took examples from this topic https://www.plus1forum.danfoss.com/index.php?topic=1525.0
By setting my INIT hardware output to constant 1 / sourcing
Then used a switch to change the pin OutputMode from 1 to 2 with an bool signal.
Does the output hardware physically allow this to function as intended/programmed? is there any risk to damage?
jashom1:
Hi Lukey,
Is the output pin on a PVG type? They can sink or source in this mode, but not sure of the current availability in this mode.
Lukey:
I've managed to get the pin to function as both sink and source with out issue on the PLUS+1 Hardware.
Issues arises with the relays I am driving externally.
As the configuration is basically 2 relays in series, the coil holding voltage once energised is high enough that the relays do not energise.
24V system, 2 relays in series, sees 12v across each coil, this is enough for them to energised.
I believe I can you some kind of diode configuration but I haven't worked out which yet.
Navigation
[0] Message Index
Go to full version