Title: PVED-CC S7 ISOBUS when CAN network is down.
Post by: jert on October 18, 2023, 09:44:55 PM
I have had a failure with our Danfoss PVED-CC S7 valves when the CAN network fails. If the valve was commanded on it keeps going even though the CAN network is down.  Is there a parameter that I can set so that if the valve loses the CAN signal it will stop immediately or go to neutral?
Title: Re: PVED-CC S7 ISOBUS when CAN network is down.
Post by: G30RG3 on October 19, 2023, 06:55:11 PM
AFAIK the PVE should generate an error after 250ms.
I guess you've set the fault monitoring to passive?
Setting this to active, should bring the PVE to a safe state in case of an error.