Recent Posts

Pages: [1] 2 3 ... 10
1
Displays / DM700 / DM1000 Ethernet Server Connection
« Last post by Mike_vd on Today at 04:47:37 PM »
Good Morning Team,

Currently considering a project that utilizes an DM700/DM1000 for logging of data and then sending this data off to a server via ethernet at the press of a button. No need for constant communication. Example once a test cycle has concluded to send the results off to a server for record.

Couple of questions:

1. Firstly is it possible?
2. Does anyone has experience with this?

Any insight/expertise would be greatly appreciated.
2
Communication / Re: BUS Load - CANOpen vs J1939
« Last post by jashom1 on Today at 01:05:01 AM »
My vote would be probably CANOpen, it gives you the flexibility to setup your devices to respond individually to SYNC messages.

For example, if you have a device that isn't required to have fast data response, configure that to respond to every 20 (or whatever) SYNC messages. The critical devices would be set to respond every SYNC message.  Using this method can help maintain your bus load.
3
Controllers / Re: Output Configured for both/either Sinking or Sourcing
« Last post by jashom1 on Today at 12:53:17 AM »
Hi Lukey,

Is the output pin on a PVG type?  They can sink or source in this mode, but not sure of the current availability in this mode.
4
Displays / Re: Data logging limitation
« Last post by Lukey on May 21, 2024, 04:25:21 AM »
Mike I am using the applog for daily logging on a drill rig, logging at 1 second intervals with more that 20 points.

The work around I have is that I create 1/the 1st point that is my 'header' of the CSV file, using Commas as my delimiter between the 'points' I am logging, this 1st point is written only once at the beginning of the log.
This is done so that when processing the CSV in excel by using 'Text to Columns' feature, each column of data then has a header for reference.

The second point is a STRING of all the points that I want to log, using a POU and instruction CONCAT, I merge all my inputs together, inserting a comma delimiter between (for the reason above), and then outputting a STRING to the applog
This 2nd point is written at 1 second intervals.

I haven't found any character limitations using a STRING in this method.

See the screenshots, my 2nd point is actually 3 STRINGS, again separated by a delimiter of a comma for processing in Excel.

I also have the CS500 in my project, yes it is completely useless for applogging/datalogging, as it can't receive strings, signed values and is limited to 31 byte messages (U31).
PLUS+1Connect Reports and Charts don't have the capabilities of the applog. Plus+1HelpDesk has told me it's in the pipeline, don't hold your breath.
5
Displays / Data logging limitation
« Last post by Mike AA on May 21, 2024, 01:33:12 AM »
I am using the applog data logging ability to frequently record machine data, unlike most who use the logging for errors and alerts we are using it for daily logging. I have nearly 30 data points that I need to log. I know about the 20 point limitation and it really hinders data analysis and makes merging data much more time consuming. Has anyone had any luck on a danfoss work around doing more than 20 points? There must be a reason for the 20 point limitation since you can log data until you run out of memory. MY current work around involves having 3 machine data logs which I still need to further manipulate taking more time.

I am using the applog like was discussed in this thread
https://www.plus1forum.danfoss.com/index.php?topic=927.msg2884#msg2884

I am investigating the data logging properties of the CS10 and CS100 but they appear to be very limited to non existant.

I started looking at external data loggers but they add more complexity by needing to convert the log file.
6
PLUS+1 GUIDE / Re: Guide Text Box Tab
« Last post by Tor on May 16, 2024, 11:46:04 AM »
Hello Scott_MARL,

I did a quick test with similar texts in v2024.1.5 and it seems to work.

Can you do some test with the latest version of PLUS+1 GUIDE as well?
If you see the same issues please report it to plus1helpdesk.danfoss.com


Thank you.
7
PLUS+1 GUIDE / Guide Text Box Tab
« Last post by Scott_MARL on May 15, 2024, 06:17:41 PM »
Using version Guide 2023.3.4.5537
The text box does not display tab as expected or consistently
I attached a photo of the text editor and the resulting text box

8
Controllers / Re: NV Memory writing error
« Last post by Tor on May 13, 2024, 07:51:51 AM »
Hello federico.furlani,

The issue with the NV_Memory was found in version 2024.1.3 and was fixed in 2024.1.4.
The recommendation is to update to the latest version of PLUS+1 GUIDE. Today it's 2024.1.5.  You can find it in the PLUS+1 Update Center.

Have a nice day.
9
Controllers / Re: MC018 C1p11 error 23 and 665
« Last post by macbahi on May 08, 2024, 02:31:45 PM »
Hello Fitz

Thank you very much to answer me.
The error it's was feedback but plus+1 compiler show other thinks.
Since I installed the last version the compilation it's not as before.

Any way thanks sir.

With best regards
mac bahi
10
Controllers / Re: NV Memory writing error
« Last post by federico.furlani on May 08, 2024, 11:13:44 AM »
Exact version is 2024.1.3.5743.

Do we need to update our installations?
Pages: [1] 2 3 ... 10