Does the gateway say CG-150 #0 Channel 0, or does it say the word "Virtual" in there? If it does say "Virtual" then you need to go up to the Communication drop down, go to Gateway->CG-150, and select from the top of the list the one that does not have "Virtual" in the name.
No it just says CG150-2 #0
I noticed the virtual on the other gateways and figured they weren't what I wanted.
I am going to ask a really silly question here, your wiring diagram looks like the CAN+ and CAN- wires are joined together at the end of the bus, is this how it is? They should not be shorted together. Otherwise your wiring diagrams look fine.
Your not in "offline" mode are you?
Cheers,
John.
I was unsure about that aswell, I've gotten in contact with the technician, to clarify.
he's told me he wired it as shown without the CAN+ and CAN- shorting together.
and that all power supply plusses and minuses are connected together in one for + and -.
I'm in online mode.
If it's a Prof1 CAN joystick (CANopen), the standard baudrate ist 125k. The controller has standard 250k.
Try to disconnect the joystick and look in the Service Tool if the status change to connected - otherwise you have to doublecheck the wiring or if the driver of the CG150-2 is installed on your PC.
Regards,
FStelzer
I tried disconnecting the joystick, it didn't seem to help.
It seems to be the driver, (I installed the CG 150 firmware update tool, and it can't find the CG150-2)
Where can I download the driver?
I downloaded PLUS+1® GUIDE Drivers v2.1.10 from Danfoss' homepage
https://www.danfoss.com/en/products/software/dps/plus1-software/#tab-overview.
and when I try to install it now it gives me this message:
"Setup detects that Plus +1 GUIDE drivers (version 2.1.11) are already installed in the folder.."
So I assumed I had all the drivers I needed