Hi Guys,
I have an application where my input is a PWM signal, the system that outputs this signal requieres to have it isolated like with an optocoupler.
does any body knows if the controller Multifunction input is an isolated input?
probably it is more a danfoss guys question but just in case
thanks
-
Hi pinias,
No, the Multifunction Input is not isolated. You need a external solution in that case.
Have a nice day.
-
I attach input configuration, hope this will help you