PLUS+1 Hardware > I/O Modules

I/O Modules on the CAN Network

<< < (2/2)

Thomas:
Hi!

Each module will need it's own node number, when they show up in the service tool the node number will be multiplied with 8.

You are using node number 64 / 8 = 8

Please make sure that you do use the latest template to the I/O module you are using, you can find them on our website.
Verify also that the Can_Config settings you have done in the template (inside the master) is matching the parameters inside the I/O module.

Here you can find more information http://www.sauer-danfoss.com/stellent/groups/publications/documents/product_literature/520l0717.pdf

Best regards // Thomas

Federico:
Hola,

Tienes más información aquí, puede ayudarte con la configuración de nodos y direcciones de los módulos de expansión:

http://www.sauer-danfoss.com/stellent/groups/publications/documents/product_literature/520l1029.pdf

Saludos cordiales

You have more information here can help with the configuration of nodes and addresses of the expansion modules:

bgtwuk:
Hi

But does the system not config the Can addressing on system power up by the voltage measured on pin 5?

Bgtwuk

Stefan:
Hello,

Yes, if you are using Address Mode 0.

Best regards
Stefan