Hi everybody,
Does anybody experienced problems with PVEP coils?
The spool is continuously moving (+/- 50%) with a constant setpoint.
The feedback indicated that the duty cycle is Ok and a similar value as setpoint.
If we use the manual lever instead of a setpoint from the ECU, the flow is continous, about +/-5%.
So manually it is correct, but not with electric setpoint!
May be somebody to help us?
We are going to try the special PVEP function block.
Thanks...
-
My mistake. PVEP is the PWM control. I originally gave you the voltage coil info.
-
Hi.
PVEP characteristics are shown below, I would try pinconfig3.
Neil