PLUS+1 Tools => PLUS+1 Service Tool => Topic started by: Scott_MARL on December 28, 2021, 11:51:07 PM

Title: Advanced Checkpoint With Namespace Active Signal
Post by: Scott_MARL on December 28, 2021, 11:51:07 PM
My system is close to max CAN bus capacity and I need to turn check points on and off when using service tool.

Applying a constant True or False boolean can be complied but if I use a set value component or a switch between the boolean constant and the "Advanced Checkpoint with Namespace" the following error comes up.

I tried compiling with Guide versions 2021.2, 2021.1, and 12.2 with the same results.

In the Plus+1 manual the A2 pin list Bool as a valid connection, is this intentional or is there a different way to interface with the check point to turn it on and off?
Title: Re: Advanced Checkpoint With Namespace Active Signal
Post by: acmall on January 04, 2022, 09:35:09 AM
The advanced checkpoints can only use a True for False constant.

From the manual
Quote
The input to A2 must only be from a True or a False component; switched True and False inputs cause compiler errors

The compile process makes this component permanently:

Active if a True component is connected to its A2 input

Inactive if a False component is connected to its A2 input

Cannot be switched between active and inactive states by the Service Tool program or through an application
.

Checkpoints only load the bus when being actively monitored. Here is a link to another forum thread where this was discussed.
https://www.plus1forum.danfoss.com/index.php?topic=1492.msg5059#msg5059 (https://www.plus1forum.danfoss.com/index.php?topic=1492.msg5059#msg5059)

If you are having issues you could try reducing the number of checkpoints being monitored at the same time.