Author Topic: MC050-055 Supply Voltage Spec Change  (Read 7004 times)

Offline dlewis

  • PLUS+1 Guru
  • *****
  • Posts: 110
  • Karma: +2/-0
    • Getman Corporation
MC050-055 Supply Voltage Spec Change
« on: March 13, 2014, 06:18:01 PM »
I was just made aware that the Supply Voltage specifications for the MC050-055/05B have changed from 9-36 volts to 9-16 volts.  >:(
This is going to be problematic for me since all my systems run on 24 volts.  I just want to bring it to the attention of everyone on the forum in case they use this controller in a 24 volt system.  I hope Danfoss doesn't start doing this to other Controllers and Displays!

Thomas

  • Guest
Re: MC050-055 Supply Voltage Spec Change
« Reply #1 on: March 14, 2014, 09:36:38 AM »
Hi dlewis!

Thanks for your question.

The recommended hardware you should use is the MC050-155. It is supporting supply voltage 9-36 VDC.
http://powersolutions.danfoss.com/stellent/groups/publications/documents/product_literature/l1301564.pdf

I hope this information helps you making the right hardware decision.

For more information please contact your sales representative.

Best regards // Thomas