« Last post by Lukey on May 15, 2023, 10:43:23 AM »Hi flno,
Yes correct OutputMode 6: PVE Output, 0 - 10000 [0.01% of PVE Power] is for driving Danfoss PVE radiometric coils.
OutputMode 3: PWM Output, 0 - 10000 [0.01% pos duty] is for driving any/generic PWM coils up to 4000hz and 3Amp, such as a proportional Cetop DCV or pressure relieving/reducing valve etc.
You will also need to use the correct Function Block for the OutputMode nominated.
There is dedicated PVE and PWM blocks found in the Outputs Library that can be used.
I wouldn't worry too much about the 10VDC you are reading I'm assuming is just the latency of your multimeter, I think you'd need a CRO to see the exact valves.
Yes correct OutputMode 6: PVE Output, 0 - 10000 [0.01% of PVE Power] is for driving Danfoss PVE radiometric coils.
OutputMode 3: PWM Output, 0 - 10000 [0.01% pos duty] is for driving any/generic PWM coils up to 4000hz and 3Amp, such as a proportional Cetop DCV or pressure relieving/reducing valve etc.
You will also need to use the correct Function Block for the OutputMode nominated.
There is dedicated PVE and PWM blocks found in the Outputs Library that can be used.
I wouldn't worry too much about the 10VDC you are reading I'm assuming is just the latency of your multimeter, I think you'd need a CRO to see the exact valves.