OILTRONIC,
At 600GPM it's only flips at 10 Hz, which is nothing.
I realized this after posting its nothing compared to my motor speed sensors which will run in the KHz.
Does the voltage measure 2300mV via multimeter or service tool? That voltage implies pinconfig=3 with both pull-up and pull-down resistors enabled, so if you had pinconfig=1 it implies the pull-down is also active.
Voltage measures both service tool and multimeter at around 2300mv. pinconfig0=1 for pull up because my flow meter is open collector.
I don't understand how enabling both pull-up and pull-down would make it work (pinconfig=3), because then I would expect 2500mV with nothing connected, and it would never trigger the default high threshold (DigThresHigh) of 3000mV. Pinconfig1=3 not pinconfig0=3
I once has a whisker short inside that blasted non-serviceable 50-pin Deutsch connector that caused similar problems. So what if you removed the connector, connected only power & CAN on pins 1-4 and then checked the pin voltage when the pin config/bias is 1?
Unfortunately I Am not around this equpment for about 2 weeks. I can double check this when I return to it
Another thought is whether the ground on the meter is the same as the MC050, which can be checked with a multimeter. I would just measure between the signal from the mag flow meter and the ground at the MC050.
The magflow meter comes directly from the box which the controller is installed in for ground and power.
I still don't understand why its 2300mv