PLUS+1 Hardware > Controllers
AnIn used as 24vdc DigIn
Lukey:
I'm trying to use the smallest size possible controller, therefor id like to use a 5v AnIn pin as a DigIn with 24vdc input. from the switch
Is it as simple as using a resistor to drop the 24vdc down to 5vdc?
Anyone done this before and can advise what size resistor they use?
*EDIT FYI, I do not want to use the 5+ from the controller or use a relay to switch the 5+.
The application requires it to be compact and simple.
acmall:
Which controller are you using? Which input pin?
It would be worth checking the ratings for the input you are using as there is a good possibility it will be rated to more the 24V. This can be found in the Controller Family Technical Information document for the controller family you are using.
Lukey:
11130915 / MC012-110, pin 5
acmall:
This is the document for the MC0xx-1xx family
https://assets.danfoss.com/documents/206067/BC152986484529en-000701.pdf
For some reason the input and output specifications are in a section with the heading CAN.
Lukey:
Thank you acmall.
Yes odd that the heading is CAN
There is mention Middle range and High range, nothing about Low range.
I have only seen the range selection on the multifunction inputs, so I'm not sure about this information.
Overall it does mention max of 36v ???
I'm not convinced.
Navigation
[0] Message Index
[#] Next page
Go to full version