PLUS+1 Hardware > Controllers
AnIn used as 24vdc DigIn
sverreo:
You can use C1p05 without a problem. The only thing is that if you input 24V it will only read maximum 5V on the input.
Make a simple logic to use this voltage as a digital input. f.ex. greater than 3V "on", and less than 2V "off"
Marbek_Elektronik:
I am not sure , but I think c1p05 at a MC024 controller maximum allowes 25V. All other inputs 36V.
Perhaps you ask helpdesk?
Lukey:
Thanks all,
Yes I will use a comparison block to simulate a DigIn on pin.
My system is a 24VDC regulated switch mode power supply so I don't expect to see anything greater.
According to the hardware manual AnIn pins rated for 36V
acmall:
--- Quote from: Marbek_Elektronik on February 20, 2024, 04:11:03 PM ---I am not sure , but I think c1p05 at a MC024 controller maximum allowes 25V. All other inputs 36V.
--- End quote ---
I think the 25V limit on C1P05 is a difference between the MC0xx-0xx controllers and the MC0xx-1xx versions.
Marbek_Elektronik:
Yes, thanks, indeed.
You are right!
Navigation
[0] Message Index
[*] Previous page
Go to full version